Kw and kvar values
Can anyone recall what the ballpark values of KW and kvar are? I can only find acceptable differences in the manual. I believe there is a formula that can calculate the values.
-
- Webmaster
- Posts: 787
- Joined: Fri Aug 02, 2002 9:03 pm
- Location: Amsterdam
- Contact:
Re: Kw and kvar values
You’ll need Paul for this one I’m afraid. I’m sure he’ll be along soon.
Buttons . . . check. Dials . . . check. Switches . . . check. Little
colored lights . . . check.
colored lights . . . check.
- 1103
- Posts: 157
- Joined: Sun Jul 13, 2003 4:14 pm
- Location: About 5 miles from Wisley Airfield
Re: Kw and kvar values
The only info I have from A4O-AB's Flight Manual is max permissible continuous load on each Generator is 36 kW, but overloads not exceeding 48kW are permissible for periods not exceeding 5 mins.
- vololiberista
- Posts: 334
- Joined: Tue Jun 15, 2010 10:13 pm
- Location: LIMZ - CUF
- 1103
- Posts: 157
- Joined: Sun Jul 13, 2003 4:14 pm
- Location: About 5 miles from Wisley Airfield
Re: Kw and kvar values
In normal ops the load sharing should remain within 2 kW/4 kVAR.
AC sys V & Freq should remain within 400 +- 10 Hz & 115 +- 6 Volts.
DC sys voltages should remain between 25 & 28 Volts.
Batt ammeter readings remain zero (normal ops)
TRU ammeter readings do not exceed 150 amps.
When starting the APU with the AC buses powered the #1 Batt must be selected to BATT ISOL prior to APU starting due to the starter motor current draw being greater than the #1 TRU fuse rating. One the starter motor cycle is complete the batt sw must be set to power on to maintain power to the APU fire protection circuit.
AC sys V & Freq should remain within 400 +- 10 Hz & 115 +- 6 Volts.
DC sys voltages should remain between 25 & 28 Volts.
Batt ammeter readings remain zero (normal ops)
TRU ammeter readings do not exceed 150 amps.
When starting the APU with the AC buses powered the #1 Batt must be selected to BATT ISOL prior to APU starting due to the starter motor current draw being greater than the #1 TRU fuse rating. One the starter motor cycle is complete the batt sw must be set to power on to maintain power to the APU fire protection circuit.
- vololiberista
- Posts: 334
- Joined: Tue Jun 15, 2010 10:13 pm
- Location: LIMZ - CUF
Re: Kw and kvar values
Many thanks for that. I'll post a "work in progress" video in the the next few days hopefully.